Hot Tubs and 2020 210.8F

Status
Not open for further replies.

dwils1980

Member
Location
Fort Collins Colorado
Occupation
Master Electrician, Building Inspector
210.8F requires all outdoor outlets to be GFCI protected. I’m running into issues with inspectors considering a spa panel with a 50amp GFCI breaker as an outdoor outlet and requiring the gfi be installed at the source to protect the hot tub and the spa panel. My argument is that the spa panel is listed as a main lug load center which I see as not requiring GFCI protection since any outdoor load centers would not require the GFCI protection. I’ve also used these same spa panels for AC condensers with a GFCI breaker feeding the condenser within the load center. I would like to know what other people’s thoughts are on this situation and if the article’s intent is to cover all outdoor electrical enclosures including load centers.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Eaton identifies their spa disconnect as a “Panel”.

Square D identifies theirs as a 2-pole load center.

Both are printed on the box and in the instructions.


Sent from my iPad using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Also 210.8 does not specify the GFCI protection has to be installed within the circuit; receptacles can be WR GFCI type, so I don’t understand inspectors logic.

Also see 680.44(A); if your tub had integral GFCI protection, no other GFCI would be required. As in, your disconnect would not require GFCI protection.


Sent from my iPad using Tapatalk
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Article 100: "Outlet. A point on the wiring system at which current is taken to supply utilization equipment"

The spa panel is part of the wiring system.

Cheers, Wayne
 

dwils1980

Member
Location
Fort Collins Colorado
Occupation
Master Electrician, Building Inspector
Eaton identifies their spa disconnect as a “Panel”.

Square D identifies theirs as a 2-pole load center.

Both are printed on the box and in the instructions.


Sent from my iPad using Tapatalk
I am very much aware of that and that has been my argu
Also 210.8 does not specify the GFCI protection has to be installed within the circuit; receptacles can be WR GFCI type, so I don’t understand inspectors logic.


Sent from my iPad using Tapatalk
The article reads that the outlet shall be GFCI protected, NEC definition of outlet reads “ A point on the wiring system at which current is taken to supply utilization equipment”, this is more than just WR GFCI receptacles but also any surface mounted enclosure outlet such as pull out ac disconnects or even a surface mounted bell box. That’s how I read this section but definitely looking for other thoughts
 

dwils1980

Member
Location
Fort Collins Colorado
Occupation
Master Electrician, Building Inspector
Article 100: "Outlet. A point on the wiring system at which current is taken to supply utilization equipment"

The spa panel is part of the wiring system.

Cheers, Wayne
So is an outdoor multi circuit load center, do outdoor sub panels require GFCI protection then?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Article 100: "Outlet. A point on the wiring system at which current is taken to supply utilization equipment"

The spa panel is part of the wiring system.

Cheers, Wayne

How would you GFCI protect an outdoor MCB load center if it was the main for dwelling?


Sent from my iPad using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I am very much aware of that and that has been my argu

The article reads that the outlet shall be GFCI protected, NEC definition of outlet reads “ A point on the wiring system at which current is taken to supply utilization equipment”, this is more than just WR GFCI receptacles but also any surface mounted enclosure outlet such as pull out ac disconnects or even a surface mounted bell box. That’s how I read this section but definitely looking for other thoughts

The point at which power is taken is the load side lugs. You have GFCI protection there. Nothing says the circuit feeding the enclosure must have GFCI protection.


Sent from my iPad using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I’d also like to point out this spa circuit is a feeder, not a branch circuit. 210.8 applies to branch circuit wiring.


Sent from my iPad using Tapatalk
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
How would you GFCI protect an outdoor MCB load center if it was the main for dwelling?
Sorry, I meant to imply that the panel is entirely part of the wiring system, and so it does not have any "points at which current is taken".

The feeder to the panel, the panel innards, and the branch circuit to the hot tub are all part of the premises wiring system. The outlet occurs in the hot tub junction box where the hot tub wiring is connected to the premises wiring.

Cheers, Wayne
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Sorry, I meant to imply that the panel is entirely part of the wiring system, and so it does not have any "points at which current is taken".

The feeder to the panel, the panel innards, and the branch circuit to the hot tub are all part of the premises wiring system. The outlet occurs in the hot tub junction box where the hot tub wiring is connected to the premises wiring.

Cheers, Wayne

I definitely misunderstood you then, sorry.


Sent from my iPad using Tapatalk
 