- Location
- Windsor, CO NEC: 2017
- Occupation
- Service Manager
Are hot tubs installed outdoors required to adhere to the equipotential bonding requirements of 680.26?
jwelectric said:A question that every electrical contractor should ask him/her self is;
Who will be held liable should someone get hurt or killed from this type of prewire installation?
That is my contention as well. If we don't do it, then we (as electricians) are committing the equipotential bonding grid to being lost once the pad is poured. IMO, the EC should make the homeowner aware of this an include it (clearly) in the bid.hillbilly said:If not you, then who?
I had lunch today with another member of the forum, rcarroll, and he brought that aspect of the situation to light. It hadn't occured to me.bphgravity said:This is going to be an issue trying to enforce. Can an inspector require an installation before the equipment is installed that requires the other installation?
Would the A/C disconnect (or whatever box is used) be a proper place to land it?infinity said:But in answer to George's question I would have them install the rebar grid within the concrete, bond a piece of #8 to it and leave it for the future. At least that way there is a reasonable chance that someone might actually connect it someday. Without it, the grid probably never gets installed.
georgestolz said:So, in this case, could an inspector reasonably enforce 680.26, or would that just open the door for disreputable EC's to install a lot of "future building" prewires?