Can a breaker used as a disconnecting means for a hot tub?
Is it "within sight" from the hot tub?Can a breaker used as a disconnecting means for a hot tub?
Can a breaker used as a disconnecting means for a hot tub?
NEC 680.12 requires 5 feet.Sure why would you think not.
Be sure it is within sight and no closer to the tub at 6 feet I believe.
I bet over 90% of hot tubs in dwelling applications are using a local GFCI breaker as a disconnecting means.Can a breaker used as a disconnecting means for a hot tub?
NEC 680.12 requires 5 feet.
Is it "within sight" from the hot tub?
I know you know but to be clear to others the NEC requires the disconnect to be at least 5' from the tub.NEC 680.12 requires 5 feet.
680.41 Emergency Switch for Spas and Hot Tubs. A
clearly labeled emergency shutoff or control switch for the
purpose of stopping the motor(s) that provide power to the
recirculation system and jet system shall be installed at a point
readily accessible to the users and not less than 1.5 m (5 ft)
away, adjacent to, and within sight of the spa or hot tub. This
requirement shall not apply to single-family dwellings
And to clarify that even further the disconnect needs to also be "within sight" which can be as far as 50 feet away, so anything between 5 and 50 is fine as long as you can also see the hot tub.I know you know but to be clear to others the NEC requires the disconnect to be at least 5' from the tub.
Also don't confuse this section that Rick mentioned with the emergency switch which is required for other than single family dwellings
And to clarify that even further the disconnect needs to also be "within sight" which can be as far as 50 feet away, so anything between 5 and 50 is fine as long as you can also see the hot tub.
The emergency switch for non dwellings doesn't have to be a disconnecting means - all it must do is shut down the pump(s). A disconnect for people servicing the pump would still be required. A disconnect could serve both purposes though.