Hot tubs
NEC 680.12 requires 5 feet.
I know you know but to be clear to others the NEC requires the disconnect to be at least 5' from the tub.
Also don't confuse this section that Rick mentioned with the emergency switch which is required for other than single family dwellings
680.41 Emergency Switch for Spas and Hot Tubs. A
clearly labeled emergency shutoff or control switch for the
purpose of stopping the motor(s) that provide power to the
recirculation system and jet system shall be installed at a point
readily accessible to the users and not less than 1.5 m (5 ft)
away, adjacent to, and within sight of the spa or hot tub. This
requirement shall not apply to single-family dwellings
And to clarify that even further the disconnect needs to also be "within sight" which can be as far as 50 feet away, so anything between 5 and 50 is fine as long as you can also see the hot tub.
The emergency switch for non dwellings doesn't have to be a disconnecting means - all it must do is shut down the pump(s). A disconnect for people servicing the pump would still be required. A disconnect could serve both purposes though.
And even more, always bring a guardian with you when using a non dwelling unit since if its you that needs to reach the emergency shutoff it will be just out of your reach.
JAP>