does an electric hot water heater need a disconnect?
does an electric hot water heater need a disconnect?
See 422 part III, and find the applicable subsection for your "water heater".
Pretty much all "water heaters" can have the branch circuit device as the disconnecting means. If it is over 300 VA and not within sight, the branch circuit device must have lockable means installed that complies with 110.25.
That information taken from 2014 NEC.
Why would you heat hot water?
disconnect required.
can be the breaker if it meets code requirements.
An $8 air conditioner disconnect is suitable for this purpose. Or if you like spending time and money unnecessarily, you can use a 30 amp double pole toggle switch ($$$) with a raised cover.
They are $5 here.
Where are you buying them for $5? Out of someone's trunk?
The company I work for always installs a 3 wire
dryer cord and plug
See 422 part III, and find the applicable subsection for your "water heater".
Pretty much all "water heaters" can have the branch circuit device as the disconnecting means. If it is over 300 VA and not within sight, the branch circuit device must have lockable means installed that complies with 110.25.
That information taken from 2014 NEC.
The company I work for always installs a 3 wire
dryer cord and plug
Why not a plug and cord connection? To disconnect, just pull the plug.
It's a waste of money to do it that way, and it's not code compliant.
What section(s) would that violate?
I've never seen a cord and plug water heater, but I always figured it was due to hardwiring, even with a disco, being less expensive.
I fail to see how that complies with 400.7...