A customr calls me they just install a new 40 gal hot water heater electric. I ask the customer who connected the unit to the electric, he wouldn't give me a straight answer. Anyway I take a ride over there check the connections at the water heater everything is ok. I do some troubleshooting and find out The connections inside the panel are burnt. I then realize they a two pole 25 amp breaker feeding the hot water heater, but only number 12 wire to the water heater. So I install a 2 pole 20 amp breaker cut off the burnt part of the wire and connect it the breaker and trun it back on, presto, problem fix. They have hot water everybody is happy, but on by way back to the office I realize that maybe that breaker and wire are not size right, for that hot water heater. I remember the name plate say 4500 watts so i divide by 240 and I get 18.75 amps. I think i am missing something is this going to be ok or do you think I will be getting a call about this. I forgot my camera sorry no pics but if i go back I will take some pics.