I have always phased the hot wires black, red and, blue or brown, orange, and yellow depending on the voltage. One of the guys i started working with doesn't even phase the hots he says it doesn't matter.
He means each system, such as in a building with both 277Y/480 and 208Y/120, should use different color groups.What about 3 phase?
It is good practice to phase all your conductors.
Easier to troubleshoot and test.
I make all my employees phase everything.
Thanks Rick
Simple answer: Yes, wherever you're sharing a neutral, and/or for line-to-line loads.So if they get mixed up it doesn't matter?
I agree that phasing coloring each phase of a system is good practice, but as George pointed out it is not enforcable for building with a single voltage system.
Chris
I have three circuits feeding 277V lighting fixtures. The home run is a 10/4 MC cable with colored conductors (B,O,Y). The MC jumpers from the ceiling j. box to the light fixtures and from fixture to fixture must match the color associated with the phase wire they connect to in the j. box, correct?
I am a Black-Red-Blue guy on 208 Y services and feeders for the following reason.
If you have a single phase 120V MC cable what color is your hot, it's Black
If you have a single phase 208V MC cable what color are your hots, Black-Red
A full 208V 3 phase MC cable your hots will be Black-Red-Blue