"Hot" wire...

Status
Not open for further replies.

cschmid

Senior Member
laszlo tell us what happened and did you play with his mind even more..I know we used to put resistors on the neutrals of plc cards and other control equipment to help drain off the voltage..the induced voltage was high enough to cause small electrical items not to work properly..but never did I receive a shock..
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
celtic said:
Here is a prime example of induction.....take a fresh roll of 14/3 ....connect ONLY the black and white conductors....like so:

Fluke87wCUoverlay.jpg
Now do the same test with a solenoid tester.
 

celtic

Senior Member
Location
NJ
LarryFine said:
Now do the same test with a solenoid tester.
celtic said:
Here is the link to a previous thread that lead to this "experiment":
Scientific Test
Since you missed the link to the thread...Not a problem...here it is :

celtic said:
Here are some pic.s from a very scientific test I performed a short time ago.

Testers used:
Ideal Circuit Tracer (Just the one piece)
Ideal Vol-Con (about 21 years old)
Fluke T2
Fluke 87
AWS Snap 8
GreenLee GT-11

....shown also is one partial roll of 14/3 NM

Testersused.jpg


I stripped back both ends of the NM and jammed the black and white wires into a working outlet ~ the red and EGC are not connected to anything...using the Ideal Tracer to show that the recept is HOT:
IdealCircuitTracer.jpg







Next...
We did NOT detect any voltage with the Vol-Con:
Vol-Con.jpg


Next....
We sensed a voltage using the Fluke T2:
FlukeT2.jpg


Next....
We sensed a voltage using the Fluke 87:
Fluke87wCUoverlay.jpg


Next...
We did NOT detect any voltage with the Snap 8:
AWSSnap8.jpg


Finally....
We sensed a voltage on the red wire...on the end of the NM that was inserted into the recept. using the GreenLee GT-11:
GreenLeeGT-11.jpg
 

ELA

Senior Member
Occupation
Electrical Test Engineer
weressl said:
...and the winner is!

Induction or capacitive coupling?
I would think that both must be considered.
The test shown here where the roll of romex is used is interesting. I would call that capacitive coupling since there is no current flowing in the conductors, thus no magnetic field to cause induction.

It would be interesting to perform this test with various load currents flowing through only the black or white wire (so magnetic fields do not cancel) and with one end of the red wire grounded (forming a single turn transformer). This would help distinquish between "induced" voltages and capacitively coupled ones.

Capacitance between the conductors will produce this "ghost" voltage that a wiggy will load down and make "disappear".

Capacitively coupled voltage can and will shock you. If the cable length is long enough and you are grounded this could be very hazardous. We have heard of GFCIs tripping when the cable length is too long (due to capacitive leakage).
 

cschmid

Senior Member
I wish it was MN live but five hrs to the twin cities means it is satellite on flat screen and cool refreshing beverages and good food..So I guess it is 90degree rated cable..
 

celtic

Senior Member
Location
NJ
cschmid said:
mn plays dallas on sunday and of course we are vikings fans here..
Dallas - 5/1
Vikings - 2/3

Where shall I send the mass card after the slaughter?
:D
 

cschmid

Senior Member
LOL I know sometimes the practice squad wins..I believe it will be a tough game as Dallas wont be able to run the ball and I doubt they can stop us from running the ball, so it all amounts to whether we stop the pass..:) :)
all of our losses have been less than one score and with a rookie QB sooner or later we shall break it out and win some..;) :smile:
I would think the hot wire should be purple and Gold....
 
Last edited:

celtic

Senior Member
Location
NJ
51647738.jpg


This is a CHEERLEADER - not a RUNNING BACK
You might want to pass this along to the coaches.


LOL
 

ZZZ

Member
We used to have a building with a 480 ungrounded delta and I would stick my finger in it occasionally to surprise my helpers. One day I tried that and found one leg had gone to ground through worn insulation. I am much smarter now:wink:
 

celtic

Senior Member
Location
NJ
ZZZ said:
We used to have a building with a 480 ungrounded delta and I would stick my finger in it occasionally to surprise my helpers. One day I tried that and found one leg had gone to ground through worn insulation. I am much smarter now:wink:

I heard that story about you too there "Lefty" :D
 