boy i'm out of touch, NONE of the examples in Appx D add in anything for the bathroom ckt, so it must be included in the general lighting load as well.
and since i'm back here again, what in the world does THIS mean?
( i have 3 ranges on one floor fed from one panel. i figure to use 14KW from column C in table220.55), i would like to know what on earth they are talking about when they say, right after Note 4:
"Where two or more single phase ranges are supplied by a 3 phase, 4 wire feeder" (which this is, at least to the panel feeding the ranges, which is what i assume they are talking about) "the total load shall be calculated on the basis of twice the maximum number connected between any two phases." [Pg 130 2011 handbook]
the maximum number is going to be one, to balance the load, so does that mean 2? i.e., since the ranges are 11.7KW, use 23.4KW instead of 14KW? that makes absolutely no sense at all to me, can anybody explain this Double Speak?
and since i'm back here again, what in the world does THIS mean?
( i have 3 ranges on one floor fed from one panel. i figure to use 14KW from column C in table220.55), i would like to know what on earth they are talking about when they say, right after Note 4:
"Where two or more single phase ranges are supplied by a 3 phase, 4 wire feeder" (which this is, at least to the panel feeding the ranges, which is what i assume they are talking about) "the total load shall be calculated on the basis of twice the maximum number connected between any two phases." [Pg 130 2011 handbook]
the maximum number is going to be one, to balance the load, so does that mean 2? i.e., since the ranges are 11.7KW, use 23.4KW instead of 14KW? that makes absolutely no sense at all to me, can anybody explain this Double Speak?