Hotel Laundry Recepts

Status
Not open for further replies.

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
2014/2017 NEC 210.8(A)(10) requires DOMESTIC laundry rooms to have GFCI protection. (B) for Other Than Dwelling Units has no such requirement. It seems a stretch to consider it an "INDOOR WET AREA". Seems like a good idea to have them protected. More chances to get "zapped" in a commercial laundry room. Don't they need protection too? …….. Just asking for a "friend". :unsure:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The 2020 code added list item 11 to 210.8(B).
"(11) Laundry areas"
No requirement in the 2017 unless they were covered by list item 5...(5) Sinks
 