Lets say you have 4 stories of hotel building. If panel L feeds lighting on each floor,panel R feeds receptacle load.If the connected lighting load on each floor is 20kW,receptacle load is 10kW and equipment load is 50kW. If you have a switchboard with a distribution section having individual breakers for lighting,receptacle panels. My idea is to have feed through panels on each floor. Do you apply the demand factor from table 220.42 for lighting,220.44 for receptacle to the total connected load on all the floors to size the breaker in the switchboard:
1.Lighting:10+30x0.4=22kW.
2.Receptacle:10+30x0.5=25kW
Breaker in switchboard for lighting=70a for 208/120v service.
Breaker in switchboard for receptacle:70a for 208/120v service.
(OR)
Do you take demand factor on each floor individual panels connected kW and then add all them up to size your breaker in the switchboard?
Each floor connected kW for lighting =20kW
Demand load=10kW
Each floor connected kW for receptacle=10kW
Demand Load=10kW
For 4 floors it will be 40kW for lighting and 40kW for receptacle which will need 125 breaker for each in the switchboard.
Which one is right?
1.Lighting:10+30x0.4=22kW.
2.Receptacle:10+30x0.5=25kW
Breaker in switchboard for lighting=70a for 208/120v service.
Breaker in switchboard for receptacle:70a for 208/120v service.
(OR)
Do you take demand factor on each floor individual panels connected kW and then add all them up to size your breaker in the switchboard?
Each floor connected kW for lighting =20kW
Demand load=10kW
Each floor connected kW for receptacle=10kW
Demand Load=10kW
For 4 floors it will be 40kW for lighting and 40kW for receptacle which will need 125 breaker for each in the switchboard.
Which one is right?