Hotel swimming pool telephone

Status
Not open for further replies.
I moved this to its own thread [MENTION=159869]Tim Dossett[/MENTION]

Afaik, the limitation is for overhead conductors but if it is closer than 5' it must be bonded. I probably would keep it at least 6' away but I am not sure that is required. Check with the authority having jurisdiction or you may have a fight on your hand.
 
It looks like this falls under "other outlets" which need to be 10' or 3.0m away from the inside wall of the pool.
 