Report on Proposals A2007 — Copyright, NFPA
2-160 Log #2734 NEC-P02 Final Action: Accept
(210.18)
____________________________________________________________
Submitter: Jim Pauley, Square D Company
Recommendation: Revise 210.18 as shown below:
210.18 Guest Rooms and Guest Suites.
Guest rooms and guest suites that are provided with permanent provisions for
cooking shall have branch circuits and outlets installed to meet the rules for
dwelling units.
Substantiation: The outlet provisions for guest rooms and suites are outlined
in 210.60 and 210.70. 210.18 is a necessary section, but is only needed to
indicate that the branch circuits for a guest room/suite with permanent cooking
provisions need to have branch circuits installed in a similar manner to a
dwelling unit. This would include the small appliance branch circuits and the
bathroom branch circuit. The laundry branch circuit is included, but an
Exception #2 to 210.52(F) would allow the omission of the laundry receptacle
if no laundry facilities are contemplated.
Panel Meeting Action: Accept
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12