I was looking at a job today at an old farmhouse that has several barns and buildings on the property. The power to the property (120/240v single phase) comes to a pole (in the driveway) with a disconnect mounted at the top of the pole. Hanging on the pole is a rod to open the disconnect. And about 4' off the ground is the meter base.
From this pole disconnect, a 3wire feeder system is ran to a barn breaker panel, the house fuse box panel, and another out building fuse box panel. So there are three separate feeders being spliced together at this disconnect location at the pole to the main feed (from the POCO transformer).
My question: Shouldn't these feeder wires to the house, barn, and outbuilding be a 4 wire system and therefore keep the grounds and neutrals separate at each location? Or does this fall under 250.32B Exception 1,2,3?
If so, does this mean that any detached building can be fed with a 3wire system if it meets 250.32B and exceptions 1,2,3?
I have always been told that I should always separate the grounds and neutrals AFTER the first means of disconnect...so what do you say?
From this pole disconnect, a 3wire feeder system is ran to a barn breaker panel, the house fuse box panel, and another out building fuse box panel. So there are three separate feeders being spliced together at this disconnect location at the pole to the main feed (from the POCO transformer).
My question: Shouldn't these feeder wires to the house, barn, and outbuilding be a 4 wire system and therefore keep the grounds and neutrals separate at each location? Or does this fall under 250.32B Exception 1,2,3?
If so, does this mean that any detached building can be fed with a 3wire system if it meets 250.32B and exceptions 1,2,3?
I have always been told that I should always separate the grounds and neutrals AFTER the first means of disconnect...so what do you say?