kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
It is a "site isolating device" and allowed by 547.9(A). 4 wire would be required from the pole top switch to the buildings by 547.9(B)(3)
EGC only required to buildings covered by 547, not a 547 building but on same site as a 547 building - it is simply supplied by service conductors - art 230 applies. If the 547 building is the only building/structure supplied the site isolating device is not required -547.9(A)(1).547.9(B)(3) says the grounding and bonding has to comply with 250.32 and 250.32(B)(1) requires an equipment grounding conductor to be installed to separate buildings.
Livestock operations have evolved to the point that you essentially have a small industrial plant these days - some supplied by 480/277 800 - 2000 amp services. Big difference from what was common back when 547 was first introduced into NEC, yet a lot of 547 hasn't really changed much over the years.
Randy Anderson (when he was still the local inspector up this way) once told me they don't consider the disconnect on the pole(provided by POCO) as the service disconnecting means even if it has overcurrent protection. I can understand the reasoning, here the POCO installs those - but they are customer's equipment because they did pay for them. But should they decide to have POCO install one of those double throw switches they do provide - those don't have overcurrent protection and my replace something that you were calling service disconnect, as well as some other situations seem to pop up once in a while that is similarly confusing on service disconnecting means. Now that was nearly 20 years ago - but seems they still look at it in the same way here, though I haven't had any recent conversation on it with any inspectors.Not quite sure what the reasoning here is, but I’ve yet to be required 4 wire at any rural distribution where an unfused disconnect or terminal box is located at the meter pole, or anywhere else. New houses are required to be inspected but are connected to the existing distribution. Three wire.
For the most part, farm buildings in this area no longer would be considered Agricultural Buildings but are still exempt from inspection. I have never seen a pole top disconnect.
What I had going on at the time Randy told me that was I wanted to connect a mobile home - it was on a rural service which did have overcurrent protection on the pole disconnect. I still had to install an additional service disconnect for that mobile home in that case as they didn't consider the one on the pole to be a service disconnecting means.