Just needing to get some ideas of going from the exterior of house panel to a garage 5-7 ft. away to put a sub-panel in the garage for a customer. Under ground, the walk is is all concrete and they do not want it cut so overhead is the only way. There is no structure between the 2 building's and not attached.
 
Texhunter7 said:
Just needing to get some ideas of going from the exterior of house panel to a garage 5-7 ft. away to put a sub-panel in the garage for a customer. Under ground, the walk is is all concrete and they do not want it cut so overhead is the only way. There is no structure between the 2 building's and not attached.

UF, EMT,IMC,RGS,ETC,ETC,ETC.
 
House have a basement? I've easily driven pipe that far. sawcut a little square out of the garage floor, dig a bit, and spin an ell on the end of the driven RMC.
 
Texhunter7 said:
No Marc, no basement there and they would like to keep it overhead. Was thinking of a riser at each location and then tri - plex betwwen the two.


Dont use tri-plex, use quad-plex. 2008 requires it anyways. Do you actually need a riser?
 
Texhunter7 said:
No Marc, no basement there and they would like to keep it overhead. Was thinking of a riser at each location and then tri - plex betwwen the two.
By the time you make your drip loops and splices at each end, for that short of a distance, it's going to look like sin. If you're going to use a riser, might as well put an RMC ell on top of each riser with a piece of RMC in between and pipe it the whole way. Just span the 5 feet with the RMC.
 
mdshunk said:
By the time you make your drip loops and splices at each end, for that short of a distance, it's going to look like sin. If you're going to use a riser, might as well put an RMC ell on top of each riser with a piece of RMC in between and pipe it the whole way. Just span the 5 feet with the RMC.



My vote is just run a steel cable between the buildings and tyrap UF to that.
 
mdshunk said:
By the time you make your drip loops and splices at each end, for that short of a distance, it's going to look like sin. If you're going to use a riser, might as well put an RMC ell on top of each riser with a piece of RMC in between and pipe it the whole way. Just span the 5 feet with the RMC.


Thats a nice arbor you have there... :D So would the building then be considered connected and not require a seperate GEC?
 
if a wiring method can be considered as the connecting means ,...then the triplex would have connected them as well.
 