Now I know why. Thanks
Why not? My total lighting load in the bathroom is 12A. The GfI recep is on a separate circuit.
210.23(A)(2) Utilization equipment fastened in place cannot exceed 50% of the branch circuit rating.
210.23(A)(2) applies to a mixed use of fastened in place loads and cord connected loads on a single circuit.
Are you saying this reference would not apply here:?
Are you saying this reference would not apply here:?
The OP has two different circuits, so it seems I am bit confused as why it would apply.
The fan combo is on its own circuit with 2 other small lights if what I read is what is the OP stating.
Correct, your lighting circuit could even feed other lighting outlets in other rooms, but as soon as you put a receptacle on it you are now in violation of the mentioned 50% of the circuit rule. The dedicated 20 amp circuit for the bathroom must also supply at least one receptacle located in that bathroom, but nothing prohibits more than one circuit to be run.Why not? My total lighting load in the bathroom is 12A. The GfI recep is on a separate circuit.
The fan/heat/light would likely require it's own circuit. For everything else, if it needs GFCI protection I would use a receptacle within the bathroom and not a circuit breaker located somewhere else.
Ditto
So you can reset it and not have to leave the bathroom if it trips. Recepts are also less costly while providing the same level of protection.Why is that?
Not saying you (plural) are wrong, just curious
ice
I have never wired a house. Today I am wiring a house ( boss's buddy ). Usually I do commercial offices or industrial shops.
[...]
As I understand it the whole rest of the house needs to be AFCI? Except perhaps kitchen GFI's and garage GFI"s..... I didn't find what I was looking for there.
Does this happen often?So you can reset it and not have to leave the bathroom if it trips. Recepts are also less costly while providing the same level of protection.
For fixed wiring like the vent/fan/heater, almost never, and if it does it is because something is wrong. Some people get too worked up over GFCI location and "what if you have to reset it?" I can't recall ever having to reset any of my indoor GFCI's other than sometimes after a lightning storm they seem to trip. Outdoor receptacles seem to have more tripping from moisture problems in equipment.Does this happen often?
Once a month?
Once a year?
Once a decade?
infinity, sierra - did you have any different thoughts?
ice
The question was about resetting receptacles, so would fixed wiring equipment be in the picture?For fixed wiring like the vent/fan/heater, almost never, ....
I agree. I don't recall ever having to reset a bathroom GFCI.I can't recall ever having to reset any of my indoor GFCI's other than sometimes after a lightning storm ....
Discussion I was replying to was about protecting said fixed equipment from a GFCI receptacle in the room vs (any) GFCI located elsewhere, so unless there is a malfunction in the fixed equipment that GFCI is likely not needing reset hardly ever unless it is also protecting receptacles - it is equipment that gets plugged in that cause so called "common tripping", the other items are just protected for worst case scenario and are rarely a problem.The question was about resetting receptacles, so would fixed wiring equipment be in the picture?
Ah - got it.Discussion I was replying to was about protecting said fixed equipment from a GFCI receptacle in the room vs (any) GFCI located elsewhere, ...
Just like this site to misread the OP and go off on a million tangents.
J.P.
#1 It is permissible to use the 20A bathroom circuit to power anything else in the bathroom as long as that bathroom is the only thing on the circuit.
#2 You do not need to put everything on the load side of the GFCI. Don't waste money on a GFCI breaker, either. Most GFCI receptacles have terminals rated for two conductors. You can feed in and out on the line side of the GFCI.
#3 It is advisable to put a separate circuit for the fan/vent/heat. GFCI protection will not be required, nor will the shower recessed light.
#4 2011 NEC means you need AFCI in almost all areas except kitchen and bathroom. Use this to plan your circuits. For instance, don't share a lighting circuit between your kitchen and dining room. Dining and living room can be on the same circuit so that you can AFCI that.
Yes.
With the correction of "receptacle" instead of "breaker".
Tapatalk!