A anbm Senior Member Location TX Occupation Designer Apr 12, 2017 #1 How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you.
How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you.
K8MHZ Senior Member Location Michigan. It's a beautiful peninsula, I've looked Occupation Electrician Apr 12, 2017 #2 anbm said: How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you. Click to expand... If put in to NEC standards, the FMC would be subject to fill requirements, where the MC would not because of manufacturing process. Cable will almost always have a protective sheath between conductors and the outside of the cable.
anbm said: How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you. Click to expand... If put in to NEC standards, the FMC would be subject to fill requirements, where the MC would not because of manufacturing process. Cable will almost always have a protective sheath between conductors and the outside of the cable.
al hildenbrand Senior Member Location Minnesota Occupation Electrical Contractor, Electrical Consultant, Electrical Engineer Apr 12, 2017 #3 anbm said: How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you. Click to expand... May I check on your question? Are you asking about Article 348 Flexible Metal Conduit? --Or-- Are you asking about Article 320 Armored Cable? When you say "(with wires)" do you mean the metal spiral is assembled in the factory with the wires already installed inside?
anbm said: How can we tell the difference between MC cable and flexible metal conduit (with wires) by just looking? Thank you. Click to expand... May I check on your question? Are you asking about Article 348 Flexible Metal Conduit? --Or-- Are you asking about Article 320 Armored Cable? When you say "(with wires)" do you mean the metal spiral is assembled in the factory with the wires already installed inside?
al hildenbrand Senior Member Location Minnesota Occupation Electrical Contractor, Electrical Consultant, Electrical Engineer Apr 12, 2017 #4 .........................