I have been looking around the 2014 revisions of the PSE&G requirement book (I just realized they made one newer than 2005 :lol
and found this:
"
7. Where it may be exposed to mechanical injury, service entrance cable of the unprotected type shall be installed in conduit, electrical metallic tubing, or protected by other approved means. Portions of a service run less than 6 in. above grade level shall be considered as exposed to mechanical injury."
So the installation in the OP wouldn't pass PSE&G's requirements.
On a different note, I figure I would mention this to you as someone else who works in PSE&G territory, they changed the wording when it comes to mounting meters. Now it says:
"J. Top of Meter Pan to Finished Grade: Min. 3 ft - 0 in. to top, Max. 6 ft - 6 in.
to bottom.**"
"** ?J? shall be 6 ft- 6 in. where sidewalks, walkways, driveways and/or blacktop is within 2 ft- 0 in. in front of meter pan. For 320 A meter pan, 6 ft from grade level to the middle of meter"
I don't know why they added "to bottom", but that confuses it for me because it should be max 6 ft - 6 in to top like it's required to be when there is a driveway or walkway within 2'.
So either it's a typo, or they changed the requirement and they won't allow a meter to be 6.5' to the top unless it's within 2' from a driveway.
This concerns me because I have come to install ALL meters at 6.5' to the top no matter where they are.