I believe that most of us know that in an ideal sinusoidal wave, the RMS value can be obtained from the peak divided by the sqrt of 2.
However, when harmonics are involved, the peak can be much higher than RMS*sqrt(2). For example, the current consumed by a rectifier contains low order harmonics (5th and 7th especially) with high amplitude.
Here is my question: how should we take these current harmonics into account when sizing the cables and the transformers? Here are my thoughts.
For cables. Assuming that the skin effect is negligible due to the low frequency of the harmonics, the main problem comes from the Joule losses. These losses are always calculated from the true RMS value of the current, regardless of the peak value. For this reason, I would NOT consider how high the peak of the current is when dimensioning the cables. For instance, if the true RMS current is 100A and the peak is 180A, I would consider the 100Arms when sizing the cable.
Different story is for the transformer. If the peak of the current is too high, we can saturate the core. If a transformer has a rated current of 100A, it means that it can handle a peak up to 100*sqrt(2)=141A. Considering the same example as above, a 100Arms transformer would not be good enough, because our peak is 180A. The equivalent RMS value of a pure sinusoid with such peak is 180/sqrt(2)=127A. Therefore, I should find a transformer that is rated for 127Arms at least.
Does it make sense, or do you have something to say against this?
However, when harmonics are involved, the peak can be much higher than RMS*sqrt(2). For example, the current consumed by a rectifier contains low order harmonics (5th and 7th especially) with high amplitude.
Here is my question: how should we take these current harmonics into account when sizing the cables and the transformers? Here are my thoughts.
For cables. Assuming that the skin effect is negligible due to the low frequency of the harmonics, the main problem comes from the Joule losses. These losses are always calculated from the true RMS value of the current, regardless of the peak value. For this reason, I would NOT consider how high the peak of the current is when dimensioning the cables. For instance, if the true RMS current is 100A and the peak is 180A, I would consider the 100Arms when sizing the cable.
Different story is for the transformer. If the peak of the current is too high, we can saturate the core. If a transformer has a rated current of 100A, it means that it can handle a peak up to 100*sqrt(2)=141A. Considering the same example as above, a 100Arms transformer would not be good enough, because our peak is 180A. The equivalent RMS value of a pure sinusoid with such peak is 180/sqrt(2)=127A. Therefore, I should find a transformer that is rated for 127Arms at least.
Does it make sense, or do you have something to say against this?