How do I politely explain "You can't use an old 2 wire 120 VAC Run without a Ground"
How do I politely explain "You can't use an old 2 wire 120 VAC Run without a Ground" to some well meaning people.
While working on some other equipment, I think I have I have stumbled upon one or two old 2 wire 120 VAC Runs with a Hot and Neutral and no Ground running through a building to a Pump and or some Light Poles.
I realize a Ground conductor should be present to carry the carry a Fault at the Lamp Pole or Pump Case back to the originating Panel Ground Bus so its Breaker will trip and personnel will be protected
I realize the Neutral is the Return Path for the Hot Conductor and goes back to the Panel to the Neutral Bus.
Unfortunately The Physics of the Panel and Breaker and how they work gets me Tongue Twisted.
Several innocent people have said with good intentions, "Why can't you just Ground at the Pump or Lamp to a Nearby Ground Rod?" At times this invites every Civil engineer and idle idiot to pipe up.
I know intuitively that you can't tie the ground conductor to a nearby Ground Rod and it has to go back to the source panel.
But how does this work? Does the Source Panel breaker somehow know that the fault has returned on its Ground Bar because the Ground Bus is to the Neutral Bus.
Exactly what happens in the Panel when that Fault comes back through the Ground conductor?
How do I politely explain "You can't use an old 2 wire 120 VAC Run without a Ground" to some well meaning people.
While working on some other equipment, I think I have I have stumbled upon one or two old 2 wire 120 VAC Runs with a Hot and Neutral and no Ground running through a building to a Pump and or some Light Poles.
I realize a Ground conductor should be present to carry the carry a Fault at the Lamp Pole or Pump Case back to the originating Panel Ground Bus so its Breaker will trip and personnel will be protected
I realize the Neutral is the Return Path for the Hot Conductor and goes back to the Panel to the Neutral Bus.
Unfortunately The Physics of the Panel and Breaker and how they work gets me Tongue Twisted.
Several innocent people have said with good intentions, "Why can't you just Ground at the Pump or Lamp to a Nearby Ground Rod?" At times this invites every Civil engineer and idle idiot to pipe up.
I know intuitively that you can't tie the ground conductor to a nearby Ground Rod and it has to go back to the source panel.
But how does this work? Does the Source Panel breaker somehow know that the fault has returned on its Ground Bar because the Ground Bus is to the Neutral Bus.
Exactly what happens in the Panel when that Fault comes back through the Ground conductor?