SF=Service factor?
I am getting some conflicting info outside this forum, but from what I am being told is that a 1200:5 CT should never exceed 1200amps?
Also as a general rule a C800 CT is good to limit the wiring to 1.2 ohms? (Yes/no/maybe? )
Thanks to everyone who has answered thus far, its been a wealth of info :happyyes:
sf safety factor
for normal operating range, yes, for a fault no
ct800 = linear to 800 v
800/1.2 = 666 A or 133 times the rated 5 A
since even an agressive bolted fault is 30-50 pu x i rated not an issue nor should saturation be an issue
so the 1.2 is conservative (but with modern relays not an issue unless crazy long leads with small wire but this is bad design)