Hmm.
I'm looking at wire size charts, and need to size a bare ground wire, to fault a 400A breaker.
What's unclear is what temperature rating to use for a bare conductor, especially if it's in conduit that makes the same connection.
What if it's in the same conduit as 70C wire and could melt that wire?
How should I think about sizing the ground?
Can I put 2 AWG on it, and call it a day?
The upstream equipment can fault more than 400A, so that current has to be able to carry all the way back to the main
breaker to get it to trip.
Ref: Current carrying capacity is defined as the amperage a conductor can carry before melting either the conductor or the insulation. Heat, caused by an electrical current flowing through the conductor, will determine the amount of current a wire will handle. Theoretically, the amount of current that can be passed through a single bare copper wire can be increased until the heat generated reaches the melting temperature of the copper
I'm looking at wire size charts, and need to size a bare ground wire, to fault a 400A breaker.
What's unclear is what temperature rating to use for a bare conductor, especially if it's in conduit that makes the same connection.
What if it's in the same conduit as 70C wire and could melt that wire?
How should I think about sizing the ground?
Can I put 2 AWG on it, and call it a day?
The upstream equipment can fault more than 400A, so that current has to be able to carry all the way back to the main
breaker to get it to trip.
Ref: Current carrying capacity is defined as the amperage a conductor can carry before melting either the conductor or the insulation. Heat, caused by an electrical current flowing through the conductor, will determine the amount of current a wire will handle. Theoretically, the amount of current that can be passed through a single bare copper wire can be increased until the heat generated reaches the melting temperature of the copper