Come through the wall of the basin with pvc conduit into a pvc j-box. I would run pvc conduit at proper burial depth and then offset up at the last minute underground to come through the side near the top of the basin. Easier to make up your j-box cord connections near the top.
Drill a drain hole on the bottom of the box. Use grease filled wire nuts pointed up.
First one for me.View attachment 23173
How do you guys do this?
Sewage lift, ejector pump. Residential.
Code wise, it's got to meet 110.25 w/in sight. This is why many are seen w/pedestal.
Listing wise, few meet the JB requirements of a methane atmosphere to 'splice' inside.
So, we drag all cords out to either proximal pedestal ,or ground box (assuming structure w/in 50')
FWIW, I just informed a local archy of the above stipulations , altered his pdf print and sent it back for 'review' , making it something like the 20th time i've asked design review focus on said requirements before bid