shockking
- Sacramento, CA
- engineer
Say we have a 1000 kVA transformer feeding an appropriate switchgear. It is 75% loaded. We want to install a 750 kW 4hr battery. If the battery is able to charge at full capacity, we would be adding 750 kW of potential load, and when used for arbitrage we could overload our transformer and gear to 150%. Not good. Alternately if we install a smaller 250 kW battery, then the battery is only able to supply a 1/3rd of the demand, defeating the backup function.
Do you have to upsize your transformer and gear to be 2X your load? Can you use controls to limit the charge rate, and create a 750 kW-discharge, 100-kW-charge battery? What am I missing?
TIA
-Tom
TIA
-Tom