How do you loop your device connections?
electricmanscott
Boston, MA
Massachusetts Master Electrician, one man show.
Quote from the installation instructions for a Pass and Seymour Trademaster receptacle.
"Loop wires around screws in a counterclockwise fashion."
:confused:
Re: How do you loop your device connections?
Loops?
I back stab...but only the other trades...
:D
:roll:
If you hold the wire at the end and looping it, the correct looping is clockwise. However, if you are holding the end of the wire and looping the wire itself the correct looping is counter clockwise. The point is that the writer has never installed a receptacle.
Does that mean that if we go clockwise, we have a 110.3(B) violation?
No. This is a manufacturer's instruction, not a listing and labeling instruction. 110.3(B) only requires compliance with instructions that are part of the listing and labeling.
Don
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling ."
Don
By your post do you mean to say that the installation instructions included with the device are not part of the listing or labeling?
Don,
I think this has come up before, but here it is again.
Installation instructions are considered to be a part of the UL listing. Check out this link to the UL site.
UL Question Corner
If this is not a typo, then the product was evaluated with the wire wrapped counter-clock-wise around the screw. Technically , that is how you would have to install it and how I as an inspector would ask that it be installed.
In reality I would never have thought to check the instructions on such a small detail.
Of course now since Scott has brought it up, I will be checking all jobs using P&S recep's more carefully. I have a 18 story condo tower using all P&S, so maybe they will have to reverse all their connections. Wow, won't I be popular!! ;)
My opinion is that it is a typo. The instructions are probably outsourced to a foreign country and they screwed up the translation.
Homer Simpson says.. "dohl"..
In other news, a local electrical inspector was killed today when he mysteriously fell off an 18 story condo project.......
So this would mean UL classified breakers can not be used as the labeling on the panels they are classified for use in do not list them. :confused:
As Don has said before UL can not have it both ways.
I have asked this at IAEI meetings of the UL rep and have been sidestepped. The answer I got was that they are evaluated for use on the panelboards specified. I have not seen this answered in print by UL.
It is a paradox.
Of course now since Scott has brought it up, I will be checking all jobs using P&S recep's more carefully. I have a 18 story condo tower using all P&S, so maybe they will have to reverse all their connections. Wow, won't I be popular!! :D :D
Seriously, I will look at the instructions, but just for curiosity's sake.