How does an electrician wire multi-floors

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
There is no limit to how many times you can tap a feeder. At some point you may run out of capacity on the feeder.

If you can keep the taps under 10 feet you can have a pretty good sized feeder as taps can be 1/10th the ampacity of the feeder overcurrent device. Tap to 100 amp panel could come off a 1000 amp feeder- sort of unlikely to tap off a 1000 amp feeder but a little more likely to do so off a 400 or 600 amp feeder.

Can't go with 25 foot tap with 100 amp conductor off a 400 amp feeder unless outdoors.
 