how does neutral (grounded conductor) really work?
ronson
rewiring 40 year old house. replacing 2 slot receptacles with 3 slots. placing a gfi at first receptacle in circuit. problem with 3 ways to kitchen ceiling light. a hot was run to one of 3 ways but with no neutral. neutral was picked up at light from another circuit. apparently this worked just fine before i got there. but with a gfi as first receptacle in circuit, the 3 ways will trip gfi. what difference does using neutral from another circuit make? i disconnected hot from circuit it was originally on and connected it to circuit that neutral from light was on. it worked fine then.
Re: how does neutral (grounded conductor) really work?
In a GFCI, the neutral and hot are compared for current flow and they need to be within ~5ma of each other or the device trips.
By grabbing another branch's neutral, the GFCI will now sense a (very large) imbalance because the neutral current for the light is no longer returning through the GFCI. In effect, this sort of situation is a hardwired & guaranteed trip. FWIW, an AFCI breaker on this light branch would also trip in similar manner.
Ronson you can't beat Tony's concise description of why you where having trouble.
Here is a graphic and link that get into more detail if you are interested.
How GFCIs Work
tony & bob, thanks for your help. please see my new questions regarding this problem in the contracting & estimating section. (this is reason why i couldn't find my original post because i placed it in this grounding section and forgot what section i put it in.)