SG-1

Senior Member
The Experiment

The Experiment

Managed to run the experiment this afternoon. Here are my results.

Some notes I take away from this thread:


The MWBC is a series/parallel arrangement of sources & loads.

In a perfect world with two perfectly balanced loads & sources no electric current would be present in the neutral or parallel section of the circuit.

The idea that the currents cancelled each other out only applies in the mathematical model, in the physical world there is no electric current in the neutral or parallel portion of the circuit, no electric current enters the node.

With unbalanced loads the series path tries to operate as a voltage divider, but a proportional electric current in the neutral keeps the voltage across the loads even.
 

Attachments

  • AMMETER_1.jpg
    AMMETER_1.jpg
    104.9 KB · Views: 0
  • TheTangle_1.jpg
    TheTangle_1.jpg
    126.6 KB · Views: 0
  • SCOPE_1.jpg
    SCOPE_1.jpg
    78.4 KB · Views: 0
  • MWBC_MEASURE img20180415_16023219.jpg
    MWBC_MEASURE img20180415_16023219.jpg
    57.7 KB · Views: 0

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
O, another MWBC debate? love these.

one thing i don't see to much about is how MWBC power is distributed. having all the loads used most often on one side of CT xfrmer is not good.

the issue with MWBC is if one load decides to run south, the load on the other side of MWBC can be damaged if both are on at the same time.
 

kwired

Electron manager
Location
NE Nebraska
the issue with MWBC is if one load decides to run south, the load on the other side of MWBC can be damaged if both are on at the same time.
Please enlighten us on this.

What exactly do you mean by load running south? We have multiwire feeds to buildings nearly all the time, loads do go south, often not effecting anything else. Now if you meant if the neutral goes south, then I get that - though like I said we have multiwire feeds supplying buildings nearly all the time so same goes for the main supply as it does for a (multiwire) branch circuit.
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
Please enlighten us on this.

What exactly do you mean by load running south? We have multiwire feeds to buildings nearly all the time, loads do go south, often not effecting anything else. Now if you meant if the neutral goes south, then I get that - though like I said we have multiwire feeds supplying buildings nearly all the time so same goes for the main supply as it does for a (multiwire) branch circuit.

MWBC with loads that are not compromised, a lost N will not be an issue, as long as both loads are on at the same time, the loads turn on and work. w/o the N one load by itself will not turn on.

take two 120ohm loads, one on one side the other on the other side. 240v CT 1ph xfrmer.
both are 1amp on half the xfrmer when only one is on. both on at the same time is still 1amp across each load with is now across the whole xfrmer. so what happens if the one load goes "bad" and is now just 60ohms. when both on you'll get more amps on the good 120ohm load, which is bad, right?

next, take 20 MWBC's, all red hots on one pole, all black hots on the other pole. now, if all the most used loads are on the red hots then you'll be loading the xfrmer heavily on only half the full winding. one half of the CT xfrmer gets real hot, the other side stays cold, etc.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
MWBC with loads that are not compromised, a lost N will not be an issue, as long as both loads are on at the same time, the loads turn on and work.
Only with equal loads; otherwise, the smaller (higher resistance) load will see higher voltage.

w/o the N one load by itself will not turn on.
If you mean if one load's switch is open (turned off) off, then none will be energized.

take two 120ohm loads, one on one side the other on the other side. 240v CT 1ph xfrmer.
both are 1amp on half the xfrmer when only one is on. both on at the same time is still 1amp across each load with is now across the whole xfrmer.
Agreed.

so what happens if the one load goes "bad" and is now just 60ohms. when both on you'll get more amps on the good 120ohm load, which is bad, right?
With an intact neutral, both loads still see 120 volts, but the "bad" 60-ohm load will pass twice the current, or 2 amps.

next, take 20 MWBC's, all red hots on one pole, all black hots on the other pole. now, if all the most used loads are on the red hots then you'll be loading the xfrmer heavily on only half the full winding. one half of the CT xfrmer gets real hot, the other side stays cold, etc.
If the center-tapped secondary was physically constructed that way, probably true.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
MWBC with loads that are not compromised, a lost N will not be an issue, as long as both loads are on at the same time, the loads turn on and work. w/o the N one load by itself will not turn on.

There's enough additional information required for those statements to make any sense that, as stated, they end up being untrue. i.e. a lost neutral will almost always cause big problems. It will cause a higher resistance load to burn up and a lower resistance load to run weak when they share the same neutral. This has nothing to do with either load being 'compromised.' Even a neutral that develops significant resistance can do it. Look at the math (see post #80).

You're probably right about badly unbalanced loads not being good for transformer longevity, but I would wager that bad cases of that are few and far between.
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
If the center-tapped secondary was physically constructed that way, probably true.

how else does a 1ph CT xfrmer get constructed? the N comes off the center point of two secondary 120v coils (or literally tied to the center of the winding during the winding process). hence the 1ph 2pole CT xfrmer.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
how else does a 1ph CT xfrmer get constructed? the N comes off the center point of two secondary 120v coils (or literally tied to the center of the winding during the winding process). hence the 1ph 2pole CT xfrmer.
You're picturing a number of turns of wire wrapped around a core, a tap attached, and then the same number of turns wrapped again. That means the first half of the winding is physically closer to the core than the second half, allowing for greater electromagnetic coupling. If two completely separately-wound coils are placed side-by-side, one coil could run even hotter than the other by being more physically separated.

Many transformers are constructed by winding with two parallel wires (called bi-filar winding), so both halves are identically coupled to the core. These two windings can then be placed in series for a center-tapped configuration, or in parallel for a single-voltage output with twice the current capacity, which describes a typical dual-voltage transformer. Of course, primaries as well as secondaries can be constructed this way.
 

kwired

Electron manager
Location
NE Nebraska
MWBC with loads that are not compromised, a lost N will not be an issue, as long as both loads are on at the same time, the loads turn on and work. w/o the N one load by itself will not turn on.

take two 120ohm loads, one on one side the other on the other side. 240v CT 1ph xfrmer.
both are 1amp on half the xfrmer when only one is on. both on at the same time is still 1amp across each load with is now across the whole xfrmer. so what happens if the one load goes "bad" and is now just 60ohms. when both on you'll get more amps on the good 120ohm load, which is bad, right?

next, take 20 MWBC's, all red hots on one pole, all black hots on the other pole. now, if all the most used loads are on the red hots then you'll be loading the xfrmer heavily on only half the full winding. one half of the CT xfrmer gets real hot, the other side stays cold, etc.
Good design is to try to achieve best balance possible. Sometimes load isn't all that predictible and this happens anyway. The more branch circuits you have the less likely you will unbalance it too severely as a general rule, but some applications can be easier to predict how loading will work out.

You're probably right about badly unbalanced loads not being good for transformer longevity, but I would wager that bad cases of that are few and far between.
Absolutely.

Heard a story one time about a new school building - three phase wye supplied. Every classroom had three rows of lights, each one was wired the same - A was front row, B was middle row, C was back row - or something like that.

They did end up having issues with the transformer because it was common to find nearly all the rooms with just the front row of lights turned on from what I was told as this was placing the majority of load on same phase.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Heard a story one time about a new school building - three phase wye supplied. Every classroom had three rows of lights, each one was wired the same - A was front row, B was middle row, C was back row - or something like that.

They did end up having issues with the transformer because it was common to find nearly all the rooms with just the front row of lights turned on from what I was told as this was placing the majority of load on same phase.
Good reasoning for rotating circuits room-to-room.
 

Besoeker

Senior Member
Location
UK
Good design is to try to achieve best balance possible. Sometimes load isn't all that predictible and this happens anyway. The more branch circuits you have the less likely you will unbalance it too severely as a general rule, but some applications can be easier to predict how loading will work out.

Absolutely.

Heard a story one time about a new school building - three phase wye supplied. Every classroom had three rows of lights, each one was wired the same - A was front row, B was middle row, C was back row - or something like that.
Is that permitted? It would mean there would be 208V between rows of lighting.
 

kwired

Electron manager
Location
NE Nebraska
Can you have a MWBC from a 277V L-N wye connection?
sure hope so -it is done a lot;)

Need handle ties on single pole or multi-pole breakers as the disconnecting means to assure you disconnect all ungrounded conductors of the circuit when you operate the disconnecting means - but that rule only was put in code maybe around 15 - 20 years ago.
 

Jamesco

Senior Member
Location
Iowa
Occupation
Master Electrician
sure hope so -it is done a lot;)

Need handle ties on single pole or multi-pole breakers as the disconnecting means to assure you disconnect all ungrounded conductors of the circuit when you operate the disconnecting means - but that rule only was put in code maybe around 15 - 20 years ago.

but that rule only was put in code maybe around 15 - 20 years ago.

Actually only 10 years ago. New for NEC 2008, 210.4(B).
And worth noting it may not have been adopted by AHJs 1, 2, 3, years or more after 2008.


.
 