I should start with saying that I trust that Bob would likely find any problem faster than I would, so I am interested in this difference in our thinking to help make me better too.
I would like to have a megger as the condition of the insulation is equally important as the Ohm meter is to continuity......In this case, the original 10/2 UF cable in truth is too small.
Then why you starting trouble?
I was not confused in the least.
What I was saying is from the beginning the op was looking for an open.
The best way to verify the conductors are open would be a simply continuity test.
There is no point in testing the insulation of conductors that are open. It is simply a wasted step.
Let's take this a step further - Let's say I ripped that T-87 out of your hands and handed you my vol-con. It rings when there is roughly a 1000Ω or less of resistance, give or take. Would you feel comfortable with the results of a test that provided you no numbers, just a ring if the reading was within a range? Would you stop investigating if it didn't ring?
Wouldn't you rather have your T-87's digital number readout?
Didn't your voltage test verify the 'open' without thinking about ohms? Why are we looking for an open?
George Stolz said:
It's an underground UF run. Chances are good that if it is indeed open somewhere between points A and B, then it's in contact with the earth.
I disagree and would not bother trying to test for an 'open' based on the assumption that the open has closed the connection to 'earth'.
Why not? In my experience, when there is no breaker tripping on an underground UF run, and no (or extremely low) voltage at the other end, there's a 95% chance that the voltage is being bled out into the earth at some point along the run, at too low a current to trip the breaker.
I would not expect to find the 5% chance that the wire is 100% wide "open", not touching anything else. So I guess what I'm saying is, I would not be looking for an open in the first place. I would be attempting to ascertain why I've got 120v on one end and 3v on the other. That condition generated the phone call.
With a good conductor surrounding my insulation (dirt around my UF), then if it passes the insulation test, I've learned two things: the insulation is great, it has a specific resistance, and if this curveball is thrown my way...
...then I have a specific cable to find, now. It has a specific resistance (unless the insulation is beyond my meter's ability to read) and from my first test I know it will hold a tone for a wire hound so I can go find the right cable and/or breaker to energize.