Only if the photocell would happen to be in series with the load, if one that connects the logic components across the line but has a separate circuit branch with a contact for the load this shouldn't be an issue. That is what the majority of the all purpose photocells most of us use are. The other style is more of something internal to an assembled item and not a general use component.
What?
you ever used one of these?
9F3A8299-406E-4986-86BB-B1E1A00A3EB6.jpeg
 

kwired

Electron manager
Location
NE Nebraska
What?
you ever used one of these?
View attachment 2560532
Yes, is the style that most of us are probably using for a general use photocell. It has full voltage input and dry contact for controlling the load. Does not depend on small amount of current through the load to make it work. Ones that do that would only be a two wire assembly, are totally in series with the load, and will have solid state switching instead of a dry contact.

My cost on that one last I checked was at least 50% what you posted. Is the one I use the most often.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Yes, is the style that most of us are probably using for a general use photocell. It has full voltage input and dry contact for controlling the load. Does not depend on small amount of current through the load to make it work. Ones that do that would only be a two wire assembly, are totally in series with the load, and will have solid state switching instead of a dry contact.

My cost on that one last I checked was at least 50% what you posted. Is the one I use the most often.
It’s a thermal type that’s not for led lights.
I don’t care how much you pay for it.
 

kwired

Electron manager
Location
NE Nebraska
It’s a thermal type that’s not for led lights.
I don’t care how much you pay for it.
Yes it is thermally actuated but not by current passing through the load.

When light hits the cell it allows current to flow through a small heater which heats a bimetal strip, that opens the load contact when it bends. When light no longer hits the cell heater current is lost, it cools down and strip bends back to close the contact.

If it is not for LED lights, it is because of contact rating and not because of how it functions.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
220515-2043 EDT

If you understood how dimmers, solid-state switches, etc, worked, and further understood about the characteristic curves of various loads, then you would know why you experience the kind of results being described.

1. Many switching devices that also need electrical power for the electronics to function, and are a two terminal device, depend on at least some leakage current thru the switching device and load to provide this power.

A tungsten filament bulb, or for that matter a carbon filament bulb, provides a very low load resistance, or moderately low resistance, when the applied voltage to the bulb is small. Thus, there is a current path with sufficient current to provide power to the electronics when the switching device has been off that the electronics can function.

If the switching or dimming device has both a hot and neutral supplied as inputs, then there is no need for current to flow thru the switching device and the load to provide power to the switching device, and the load impedance can be as high as you want and the switching device will still work.

A tungsten filament bulb has a room temperature off state resistance of 1/10 or lower than at its stated operating voltage. My measurements on a 100 W 120 V bulb are 10.3 ohms with a Fluke 27 at room temperature, and calculated resistance at 120 V and 100 W is 144 ohms.

This change in resistance is from the change in filament temperature. But at both temperatures the filament can be considered a linear resistance.

What does an LED look like from a resistance perspective, it is a nonlinear characteristic. Three different manufacturers of 9 W 120 V LEDs all read about 5,000,000 ohms with the Fluke 27. Polarity did not matter. I have not measured at higher voltages.

You have to know how different devices work and their V-I characteristics to make any useful judgements.

.
 