He did measure the potential at the very beginning. About 1 foot away from the rod IIRC it was about 100± with current at .42 amps. So, lean against the box and you'd have about 20VAC between you and the ground.
Not just the box.... If I understood Mike correctly the siding on the structure is steel.
As for your post, the test you described has nothing to do with the touch potential tests Mike preformed later in the video. (Time marker 20:56).
Though the test you referred to was a step potential test where mike measured, I belive, 104Vac. More than enough to deliver an electrical shock or worse. Mike even mentioned the possible danger of the test.
Go to time marker 20:56 on the video,
Touch Potential.
https://www.youtube.com/watch?v=Yg6G5VUSsWA
Using one ground rod with the hair dryer set at high Mike measured 30Vac. Ground rod is 50ft deep. Ground resistance? I believe the 50' rod that mike used for the test was the one that measured 16.4 ohms.
Note, with both rods in parallel, (total ground resistance was 10.8 ohm), the touch voltage measured 20Vac. What did mike say? The lower the ground resistance the lower the touch potential, voltage.
Correct.
Using the same touch potential test experiment mike used, instead of using the hair dryer use an 8 ohm resistor in its' place? What will the touch potential, voltage, measure, if the ground resistance of the 10' ground rod is 265 ohms? At 265 ohms any guess what the entire outer metal skin of the building voltage was above ground? The amount of touch potential, voltage, would depend on if there was a heavy dew the night before.
.
(NOTE: Mike may have only said the siding was made of steel as an example for running his tests, and it actually is not.)
..