I am still working on correcting all the violations on this pump house I've been upgrading. One thing has me puzzled...
The two 3-phase 230VAC pump motors are large (100A and 60A respectively), so they are on 125A fused branch circuits with 4AWG conductors (the conductors for the 100A motor are currently undersized, but that's a separate problem I'm addressing).
The part that has me concerned is that, for each motor circuit, there are 12AWG taps (230VAC) off two of the hot phases of the motor branches; these taps are for controlling the starters for the motors. That means the hot 12AWG conductors have no overcurrent or short-circuit protection other than the 125A TD fuses that protect the motor branch circuits. How can this be code compliant?
On the 100A pump motor, this 12AWG wiring appears to have been installed at the factory inside the panel containing the fuses, starter, and motor overcurrent device. However, the wiring was modified... the control wiring was extended to a third-party automated pump controller.
So the "unprotected" 12AWG control circuits for both pump motors now pass out of their respective motor starter panels to a separate "master" pump control panel mounted several feet away. If it's a consideration, the pump installer used moisture-tight flexible (nonmetallic) conduit to route these control wires (without any ground).
It just seems wrong to me that 12AWG conductors are tapped off a 125A fused circuit.
The two 3-phase 230VAC pump motors are large (100A and 60A respectively), so they are on 125A fused branch circuits with 4AWG conductors (the conductors for the 100A motor are currently undersized, but that's a separate problem I'm addressing).
The part that has me concerned is that, for each motor circuit, there are 12AWG taps (230VAC) off two of the hot phases of the motor branches; these taps are for controlling the starters for the motors. That means the hot 12AWG conductors have no overcurrent or short-circuit protection other than the 125A TD fuses that protect the motor branch circuits. How can this be code compliant?
On the 100A pump motor, this 12AWG wiring appears to have been installed at the factory inside the panel containing the fuses, starter, and motor overcurrent device. However, the wiring was modified... the control wiring was extended to a third-party automated pump controller.
So the "unprotected" 12AWG control circuits for both pump motors now pass out of their respective motor starter panels to a separate "master" pump control panel mounted several feet away. If it's a consideration, the pump installer used moisture-tight flexible (nonmetallic) conduit to route these control wires (without any ground).
It just seems wrong to me that 12AWG conductors are tapped off a 125A fused circuit.