On the new hospital where doing, we have a 150 kva xmer that has 412 amps on the secondary, how can the enginneers have us hooking this up to a panel with a 800 amp main. what gives?????
On the new hospital where doing, we have a 150 kva xmer that has 412 amps on the secondary, how can the enginneers have us hooking this up to a panel with a 800 amp main. what gives?????
Primary protection is only part of what is required...augie you are correct after finding the other half of this ripped print I now see the primary at 225 amps... thanks..