I was asked in class, when the supplementing the water pipe as GES was added. What code cycle was that implemented? Thanks for your time, and besides having all previous NEC's where would I find this info? Thnaks again
 
1978 as an absolute, 1951 (or 1949, 480sparky?) as an "If".

2581 1947
A continuous metallic water pipe shall always be used as the grounding electrode where such piping is available.

2581 1951
A metallic underground water piping system, either local or supplying a community, shall always be used as the grounding electrode where such a system is available. If the buried portion of the metallic piping is less than ten feet (including well casings bonded to the piping systems) or there is some likelihood of the piping system being disconnected it shall be supplemented by one or more if the grounding electrodes recognized in Sections 2582 and 2583.

250-81 1959
. . . Where the buried portion of the metallic piping is less than ten feet (including well casings bonded to the piping systems) or there is some likelihood of the piping system being disconnected it shall be supplemented by one or more if the grounding electrodes recognized in Sections 250-82 and 250-83.

250-81 1968
. . . Where the buried portion of the metallic piping is less than ten feet (including well casings bonded to the piping systems) or there is some likelihood of the piping system being disconnected or insulated through the use of nonmetallic piping or insulated coupling, the piping system shall be supplemented by one or more if the grounding electrodes recognized in Sections 250-82 and 250-83 . . .

250-81 1971, 1975
. . . Where the buried portion of the water pipe (including any metal well casing effectively bonded to the pipe) is less than 10 feet long or where the water pipe is or is likely to be isolated by insulated sections or joints so that the effectively grounded portion is less than 10 feet long, it shall be supplemented by the use of an addiional electrode specified by Sections 250-82 or 250-83 . . .

250-81(a) 1978
. . . A metal underground water pipe shall be supplemented by an additional electrode of a type specified in Section 250-81 or Section 250-83. . .

250-81(a) 1993, 1996
. . . A metal underground water pipe shall be supplemented by an additional electrode of a type specified in Section 250-81 or Section 250-83. . .

Of course, this took a while to type . . .
 