tryinghard said:These are underground locations, how about above ground? Indoors?
Looking at ('05) 334.12(B)(4)...Where exposed or subject to excessive moisture or dampness
Then refreshing ourselves in Article 100:
Location, Damp.
Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some coldstorage warehouses.
Location, Dry.
A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
Which brings us back to 334.10(A)(1)
Type NM.
Type NM cable shall be permitted as follows:
For both exposed and concealed work in normally dry locations except as prohibited in 334.10(3)
Which brings us back to my question:
What type insulation is on the conductor.....is it listed in 310.13?
Does it have a "W" in it (ie, THWN)?