zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
They can do that somewhat reliably for a stead load, but changes in load will throw it off. If you have "down days" with little or no load the voltage can possibly be higher then desired during those periods. Times with even more load than designed for will result in lower voltage.
roughly every 100 ft will require a wire size upgrade. for long runs, the utility may change the taps for you but with limits. they can usually go 2 up or 2 down at 2.5% per step. however, they are usually compensating for primary drop, not secondary drop. with a dedicated transformer, they may consider changing the tap but should look at voltage regulation and voltage at minimum load.
utilities usually compensate for secondary drop with bigger wire or sometimes a bigger transformer and may expect you to do the same. the bigger transformer will help secondary regulation but they probably will ask you to pay for the upsizing.
Thanks for bringing this up! I agree if adjusting the secondary taps setting shall be based on the minimum load.
If adjusting utility transformer 2 up at 2.5% per step which is 208*1.05 = 218V, will the higher voltage at "down days" cause problem? I think almost all 2 pole home appliances are rated at 208V -230V and the voltage fluctuation is also not a problem for the 200V motors some times? Will 120V*1.05 = 126V be a problem for 120V appliances?