hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
Because of the mountains, most of the lines are single phase spurs off the main line, going many miles, then just end.. What does that mean?
Because of the mountains, most of the lines are single phase spurs off the main line, going many miles, then just end.. What does that mean?
Isn't it possible to have more grounding make things worse? With a lightning event, you can have ground potential rise, and it seems logical that the "better" grounding you have than the more of that rise your electronics will see.I suspect that the changes @hillbilly1 made helped his customers. However I am of the opinion that the bonding was the primary reason for the improvements, and the ground rods secondary at best.
I've had one experience where ground rods without bonding apparently caused a problem. Service entrance with ground rods on one side of the building, Telco demark with its own ground rod on the other side of the building. No bonding between them.
No evidence of external damage, but a section of phone wire inside the building looked like a Christmas decoration. Every few inches there was a jagged copper spike sticking out of the wire, with a single mark on the wood behind it.
Isn't it possible to have more grounding make things worse? With a lightning event, you can have ground potential rise, and it seems logical that the "better" grounding you have than the more of that rise your electronics will see.
Even in high amperage service like 3000A?
The one below the rock quarry the bonding issue was a major component, but the others were not bonding issues.I suspect that the changes @hillbilly1 made helped his customers. However I am of the opinion that the bonding was the primary reason for the improvements, and the ground rods secondary at best.
I've had one experience where ground rods without bonding apparently caused a problem. Service entrance with ground rods on one side of the building, Telco demark with its own ground rod on the other side of the building. No bonding between them.
No evidence of external damage, but a section of phone wire inside the building looked like a Christmas decoration. Every few inches there was a jagged copper spike sticking out of the wire, with a single mark on the wood behind it.
My thinking is the number of different scenarios are numerous. For example, is lightning traveling on one of the conductors (and if so which one), or is it a ground potential rise issue. If so, what is the relative location of the building ground and the ground referencing the electrical system. are there multiple electrodes, where are they relative to the ground potential rise. Is the voltage of the electrical system between conductors still the same it is just the ground potential has risen? Just lots of different scenarios and I can envision situations where the more electrodes and more grounding you have, you are going to see more of that ground potential rise and get more damage to equipment.With sufficient bonding I don't see ground rods hurting, because everything will experience the same elevated voltage.
But if you don't have bonding IMHO more ground rods would make things worse. In the example I saw, perhaps not having the telephone company ground rod would actually be safer.
I directed the installation of over 200 remote communications shelters to Motorola Standard R56 - Standards and Guidelines for Communication Sites. [No the US National Electric Code (NEC) is not the do all and end all of everything electric and electronic. Imagine that.] I never lost operational time to a lightning strike and in radio communications height is might. You site the shelters on the highest bit of real estate that you can get the use of. Lightning strikes to the towers with attendant side flashes to the shelter and dozens of conductors for many different purposes passing from things outside the shelter to things inside the shelter are not rare.So with all the grounding on the line, probably hundreds of ground rods (depending on how big an area we want to bring into it of course). You think a couple more is going to make any difference? Also if the lighting hits the ungrounded conductor, which is usually on top and more likely I would think, more grounding of the neutral isn't going to change anything.
Not according to the National Institute of Standards and Technology (NIST). See their publication "Getting to Earth."Isn't it possible to have more grounding make things worse? With a lightning event, you can have ground potential rise, and it seems logical that the "better" grounding you have than the more of that rise your electronics will see.
Steel or concrete poles, no, but many are wood poles.I don't know about the OP's situation but the ball field lighting I have done had anywhere from 12' to 30' deep 24" to 36" diameter pole bases loaded with rebar, it's doubtful a few rods would make any difference.
The utility installed some steel poles for a 138kV line. The poles had a concrete base about 8' in diameter, 25' deep. It had 1" vertical rebar on 12" centers about 18" in from the outside, and 3/4" horizontal rebar rings on 8" centers, with the 15 or so anchor bolts attached to the rebar cage. They still install a 10' ground rod with 4AWG to the steel pole!I don't know about the OP's situation but the ball field lighting I have done had anywhere from 12' to 30' deep 24" to 36" diameter pole bases loaded with rebar, it's doubtful a few rods would make any difference.
Surge protector at the service equipment may have solved those issues as well.You can’t say ground rods are absolutely worthless, I’ve had several jobs where they had lightning issues, and adding ground rods and proper bonding solved the problem. I have a neighbor that lives on top of a hill that all pasture, no trees. His fence charger got knocked out every time a storm came up. Installed two rods at the barn, two at the house, and two at the utility pole feeding the house. He hasn’t replaced a charger since. Another customer had a house below a rock quarry, lightning constantly taking out his tv and telephones. The phones and cable drops were at the opposite end of the house from the service, and were not bonded to the service. Added a rod at both ends, and buried a #4 bare copper between them. He hasn’t had a problem since.
Another customer was at the end of the poco line, and was constantly getting surges during storms. Added three rods, and problem stopped.
If you have a rather direct hit, you are screwed, if it strikes nearby, like a pole a quarter mile away, any rods between you and the strike are absorbing some the energy, if you happen to have surge protection it hopefully minimizes the effects within your premises wiring.. What does that mean?
So with all the grounding on the line, probably hundreds of ground rods (depending on how big an area we want to bring into it of course). You think a couple more is going to make any difference? Also if the lighting hits the ungrounded conductor, which is usually on top and more likely I would think, more grounding of the neutral isn't going to change anything.
This was back before surge protectors were common place. None were installed at those locations. Next week putting one in at a poultry transport facility, wood building with metal roof and siding. They said they had a ground rod drove at each corner, but I haven’t seen how they are connected yet. They claim lightning runs along the conduits and out of the outlets.Surge protector at the service equipment may have solved those issues as well.
Those test wellls will never be opened once you terminate them.I agree. The client doesn't know any better that's why they hired professionals to do the design in the first place. We did a huge apartment building with probably 2000 linear feet of footings with CEE's. They also had us install at least ten of the 3/4"X10' triangle rod nonsense with grounding test wells in the basement. Talk about a waste of money.
I don't necessarily buy that. One time incident maybe but not something that happens more than one time.They claim lightning runs along the conduits and out of the outlets.
Not according to the National Institute of Standards and Technology (NIST). See their publication "Getting to Earth."
.
I’m kinda suspicious of it too, there are two grain silos next to the building on a different service, and they say they’ve had no problems there. I have no doubt the conduits are not complete, and have romex pulled into them. I haven’t opened up the panel yet to see what kind of nightmare it is. The silos are newer, and looked like they were professionally done. I know it wasn’t a local because it’s all in rigid and looks good!I don't necessarily buy that. One time incident maybe but not something that happens more than one time.