Laying out circuits residentially I would figure a receptacle at 180 va..
well found out a couple years back that was not correct.
The amount of receptacles installed are based on the area as per load calculations for general lighting @ 3va.
That being said. How do you do that?
Guessing here....
Lets say I want to run a 15 amp circuit.
15a x 120v = 1800va
1800va / 3va = 600sq feet
25' x 24' = 600 sq feet
If I where just installing receptacle outlets, would that mean that if I where placing receptacles in a 25' x 24' (600 sq ') room that circuit could not leave that room and feed other rooms?
Or that one circuit could feed receptacles in four 12.5' x 12' ( 150 sq ' x 4 = 600 sq ' ) rooms? (someone please help with the math here, my math is showing four rooms but it looks like 25 and 24 halfed at 12.5 and 12 should be two rooms not four ???)
Is this correct?
Thank you