charlesaf3
Member
- Location
- Richmond VA
yep, isn't that always the wayHe won't take the time to read it with you. He just gets mad when you question him on something.
yep, isn't that always the wayHe won't take the time to read it with you. He just gets mad when you question him on something.
I would love that. He actually said he couldn't think of a code reference prohibiting it, but wouldn't accept it unless I cold provide a code ref specifically allowing it.Seems every year there are more and more inspectors who make "seat of my pants" calls. It should be mandatory that any rejection should be accompanied by a Code reference.
For residential I had a check list that covered 90% of the potential violations and had the Code reference by each item
Tell him to go to the local hospital and count up the number of normal branch panels fed from the Normal Power Main disconnecting device.His theory is that we already have 400 amps of "primary" subpanels, and that the collective amperate of the subpanels cannot exceed that of the disconnect/meter (ironic since the meter is a 320 of course)
You have to pick your battles, if it’s nothing major, you change it and go on. I had an inspector illegally require a neutral/ground bond on the load side of a groundfault protected transferswitch. He was stead fast on wanting it, so I did it, then changed it back after he left. I would have been hung with the responsibility when the ground fault switches didn’t work because of it.I would love that. He actually said he couldn't think of a code reference prohibiting it, but wouldn't accept it unless I cold provide a code ref specifically allowing it.
Charles, I'm in Richmond (Henrico), too, for decades. Most of the inspectors I knew by name are gone.Yeah, that's our take. Exactly my thought on the breakers. But he needs a code section..
That's not how the NEC works. Very little of what we may do is spelled out.He wasn't being mean about it, just said he needed a specific code section justifying.
I'm sorry, but my position is exactly the opposite. I won't kowtow to a bad call even if it will only cost me a few minutes . . . this time. It sets a bad precedent and almost guarantees that the same thing will happen again, which costs us more time and money.While I strongly agree with you, you do realize what kind of life I'd have going forward? I have a firm policy that if inspectors tell me something I disagree with, but will only take me a few hours, it's much better to take those hours to do the thing than it is to take those hours to fight with the inspector. And god only knows how many hours in the future...
Again, that's not how the NEC works.I would love that. He actually said he couldn't think of a code reference prohibiting it, but wouldn't accept it unless I cold provide a code ref specifically allowing it.
Actually he needs to find a code section that supports what he is claiming. There is nothing that limits number of circuits/feeders that can be supplied by an overcurrent device it only has to be able to handle the load connected to it and can factor in demand or other time of use situations as well if those things end up assuring total demand at any point in time is low enough the device can take it.Yeah, that's our take. Exactly my thought on the breakers. But he needs a code section..
because those well qualified for the job want to work where they will earn more $$$How does someone get to be chief electrical inspector of a major city yet be so off base on something basic and about how the code works? Crazy.
So you spend all this time learning theory, code and other aspects of electrical are required to pass a test to get a license then most usually need to take certain amount of continued education to be able to keep said license, but an ignorant inspector can basically make all that somewhat meaningless because he doesn't want to learn what is right and just hide behind his authority?While I strongly agree with you, you do realize what kind of life I'd have going forward? I have a firm policy that if inspectors tell me something I disagree with, but will only take me a few hours, it's much better to take those hours to do the thing than it is to take those hours to fight with the inspector. And god only knows how many hours in the future...
Most places if he isn't going to pass it, he needs to write up some kind of notice stating what the deficiencies are and provide references to the code or local rules that make it a deficiency. How is he going to do that if he doesn't even know if it is a deficiency?I would love that. He actually said he couldn't think of a code reference prohibiting it, but wouldn't accept it unless I cold provide a code ref specifically allowing it.
While I strongly agree with you, you do realize what kind of life I'd have going forward? I have a firm policy that if inspectors tell me something I disagree with, but will only take me a few hours, it's much better to take those hours to do the thing than it is to take those hours to fight with the inspector. And god only knows how many hours in the future...
Discussion with chief inspector (city of Richmond VA, TJ if you are here, not Tab, he's gone)
Just for clarification what size feeder did you supply the house withPlan B isn't the end of the world, we'd come back to a 100a sub in the garage off one of the 200s using mobile home feed (allowed here for residential)
You could present him with 230.40 exception #3 and show him had you douple luged the load side of a 400 amp meter you would not have even needed overcurrent protection at all as far as the load was concerned and you would have been able to supply the garage with a 3 wire service entrance as well as the house with a 3 wire service entrance.Discussion with chief inspector (city of Richmond VA, TJ if you are here, not Tab, he's gone)
That was always my approach and it usually worked. You have to know the code. If the inspector doesn't think you know what you're doing they will lean on you harder.My usual strategy in that situation is to do both. Push back and argue politely while still making the correction. Allows them to save face on the current permit but discourages them from asking for the same unfounded correction in the future. Acknowledges their authority while reminding them there are limits to it. Results can be hard to guage in the short term but in aggregate it seems to work over time.
this wouldn't be a problem in Henrico. Have you worked with TJ?Charles, I'm in Richmond (Henrico), too, for decades. Most of the inspectors I knew by name are gone.
He needs a code section to say you're not in compliance with.
I don't believe so, but I haven't had any inspection problems or disagreement in the city in many years.this wouldn't be a problem in Henrico. Have you worked with TJ?