The question came up over a 50amp SquareD Homeline breaker, the A/C was causing the breaker to trip frequently and the homeowner indicated that he had reset the breaker numerous times. After recommending the replacement of the breaker the question was posed "How many times can it trip before it must be replaced?" I didn't have the specific answer, hence my question to the forum.
I am understanding from the previous post that most molded case breakers can be switched (mechanical operation) approx 1,000 times but can only trip (fault interruption) 2-3 times before replacement is recommended.
Thanks for the info.
my opinion, unmarred by any research or factual knowledge whatsoever,
is that with 10k interrupting capacity breakers of the type usually used
in home panels, when a breaker has been habitually overloaded and
repeatedly reset, it loses its spunkiness, and begins tripping at a lower
set point than the rating of the breaker. it starts feeling mechanically
unsound as well when you reset it, and sometimes won't reclose at all.
these are the symptoms of creeping breaker sickness. time to bury it,
and put another $5 breaker in.
for big breakers, rack in breakers, and such, go ask zog.