- Location
- Wisconsin
- Occupation
- PE (Retired) - Power Systems
As always we have people talking about 15 amp SP breakers at a home and some talking about large commercial / industrial breakers. Now there is nothing wrong with that except it makes the thread hard to follow and tough to know what the answer is.
The difference is not between residential and commercial/industrial as far as the breaker is concerned. UL489 and NEMA AB1 tests apply to all molded case breaker regardless of their application. The Square D Homeline breaker quoted by the OP is tested to the same standards as the one in the picture posted by Brian John.
The difference comes in when we consider how much current may have been interrupted and then how much current will need to be interrupted if the breaker is closed onto a fault. It is unlikely that a single family residential breaker will ever see a "short circuit" in its branch wiring that will come close to the maximum ampere interrupting capacity of the breaker, however the same cannot be said of commercial and industrial applications.
The OSHA proscrition against resetting a breaker effectively says you must figure out why the breaker tripped before it is reset. If you have a breaker feeding a counter top that trips whenever the microwave and the toaster oven are operated at the same time you may simply turn off a device and reset the breaker. If a breaker has tripped with no explanation then troubleshooting should be performed prior to resetting the breaker.