kw to volts
First of all, Welcome to the Forum, JW.kw to volts
kVA = kilovolts * amps
pf = power factor = cosine of the angle between the current vector and voltage vector
kW = kilovolts * amps * pf
pf = kW / kVA
In other words, we are missing two input values needed to answer your question: the amps and the power factor.
Ow! Just thinking of boiling down to the equivalent diagram hurt my head.. . . if you were to Thevinize the grid . . . .
Ow! Just thinking of boiling down to the equivalent diagram hurt my head.
If sizing equipment, you should find out. I have seen industrial feeders with a 65% power factor.How often do you really know the power factor. Afterall it is determined by the load. I usually omit it but if I feel the need to include it I usually defualt to a .8 PF.
I heard once....and I have no idea how they came up with this. But if you were to Thevinize the grid you would end up with about a .8 PF. I assume that is why most generator, transformer nameplates have a KW rating based on a .8 PF.
If sizing equipment, you should find out. I have seen industrial feeders with a 65% power factor.
My house has two panels, one leg at 79%pf, one at 95% pf, and the other two at 98-99% pf. That will vary, of course, as the loads change.
The 80% pf on a generator is a blanket assumption, but must be validated with some analysis of the type loads being served. You may find you will have to de-rate the generator from the 80% pf rating.
Transformers are rated by kVA or VA, etc.
I liked doing Thevinin equivalent diagrams. . . they were satisfying to the part of me that also liked diagramming sentences.
Never really thought about the grid that way until I read your post. The image in my mind just kept opening like a fractal view burrowing smaller and smaller.
They even have var plants.Afterall, all the POCOs know the PF at each of their plants.
They are not Thevenizing the grid to get the power factor, they are measuring vars. And I doubt it is any where near 80%. The transmission system will have better var maintenance than that.
A city might be 85% or it might be 95% or who knows what, but they will try to get to the 90's.
There are diminishing returns after you correct much more than the low to mid 90's (i.e. there is a knee on the return graph).
Individual loads that the EC may deal with could be most anything so need to be looked at closely sometimes.
Well, yes but.....kVA = kilovolts * amps.
Then use kVA = volts*amps/1000.Well, yes but.....
Many of us deal with kVA but not routinely with kV.
The magnitude of the Volts and Amps product that we encounter makes kVA just a more convenient measure.