kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
If he already has 2-225 amp feeders, just connect them in parallel and use a 400 amp breaker for feeder breaker. Can only have one feeder to the separate building but it can have up to six disconnecting means at the separate building.Again, if need be, run a 400 amp breaker, 500 MCM wire and a 400 amp panel.