The NEC junction box fill numbers are very conservative when there is no device in the box, a good electrician can shape them in and exceed the NEC limits without an issue. However IMO the OP's box is excessive.
 
Did a job a few years back at a commercial building that suffered fire damage.

Was doing tear out and pulled down a piece of 3/4" emt that was located in an area where excessive damage was done.

When I cut through it with a sawzall there was literally no air space in the tube even after all the insulation burned off.

I saved it for the electrical inspector to look at.

There was over 20 conductors, mixed 10's and 12's.

Whoever pulled those in must have heated up the tube to expand it and froze the wires shrink them.

We found most all the conduits and boxes were excessively over filled.

It was a Quick Lube station and surprisingly the fire was attributed to solvent soaked rags left in an unapproved container.

The electrical was very forgiving in that building.
 
The j-box feed a series of plugmold strips set up for a large wall mounted lighting display for a locally owned BB store.

Who installs those? Would it be someone from fixture supplier? They mounted the front half of strips then left the back cover off. Hopefully it wasn’t an area EC.
 