J Joao Member Location portugal Occupation engineer Sep 18, 2025 #1 How much electric power is needed for HOT commissioning for a HV Substation? For example: 1 x 400 kV GIS with 10 bays 2 x power transformers 600 MVA, 400/225 kV 1 x 225 kV GIS with 10 bays Control Room with P&R System + SCADA + DC System + UPS
How much electric power is needed for HOT commissioning for a HV Substation? For example: 1 x 400 kV GIS with 10 bays 2 x power transformers 600 MVA, 400/225 kV 1 x 225 kV GIS with 10 bays Control Room with P&R System + SCADA + DC System + UPS
D Deltaforce Senior Member Location India Occupation Electrical Engineer Sep 19, 2025 #2 300kw to 800kw auxiliary power Specific equipment manufacturer data and project specifications depend
300kw to 800kw auxiliary power Specific equipment manufacturer data and project specifications depend