fastline
Senior Member
- Location
- midwest usa
- Occupation
- Engineer
I got a call but have not yet been onsite. Customer is on rural 1P. He requested 400A, which is broke down to 200A to a home and 200A to his shop. This is all being fed with a 50kva pad transformer. Complaint is when starting and running a big air compressor, it will struggle severely. When running, the current on the line is 130A. Obviously inrush has to be evaluated here but I am wondering how hard you can pull on that transformer before significant voltage drop occurs? I am sort of suspecting primary sag but again I have not been onsite yet. I do know after a struggle to start, the 200A main break has opened a couple times. To me that sounds like severe voltage drop where the load cannot accelerate, causing high current long enough to open. Just a hunch.
I've generally figured that 150% OL is fine for a transformer and I know POCOs push them extremely hard feeding homes.
I've generally figured that 150% OL is fine for a transformer and I know POCOs push them extremely hard feeding homes.