Here is where I'm at. After testing, I feel comfortable that the primary and transformer and performing admirably. Here is the first issue. Primary comes in and hits the dedicated 50kva xfmr and fed out on two line sets, one for house, one for shop, both with 200A mains right at the xfmr. That is an issue as the 200A breaker is getting trippy with big motor starts. The lineset is 4/0 Al and I need a bigger breaker on that! Can someone kick me a code compliant way to get this done? The panel in the shop also has a 200A breaker but has never tripped. Personally, I feel the breaker is not right but it also needs increased so that is not tripping. This is mostly an inrush issue, not FLA issue.
If you have two 200A breakers in series, and only one is tripping during motor starting, then the first step before upsizing the breaker is to ensure that there isn't a problem with the breaker or its attachment.
It may be that the two breakers are in different parts of the allowed tolerance band and the more sensitive breaker is tripping.
But the other possibility is that something is causing excess heating at one breaker, making it prone to tripping.