Note to greg1707:
1. Under 2011 NEC, a refrigerator in a residential kitchen is not required to be GFCI protected. It can be on a SA circuit upstream from the GFCI. I think good practice is to run a separate unprotected 20 amp circuit for the refrig.
2. If you ran a 15 amp separate circuit for the refrig and it had GFCI protection, the GFCI device would be behind the refrig. I think this is a Code violation because it is not readily accessible. (if you have a GFCI breaker, that is Code legal.)
3. I think it is a bad idea to run a 15 amp circuit to two stationary appliances that are rated 11 amps and 6.7 amps. That is 17.7 amps. But it may not be a violation. There is a rule that a dedicated circuit to one appliance is limited to 50% of the circuit rating, but I do not think that applies to two appliances. (but it should)
4. If the manufacturer requires a separate 15 amp circuit, it is a Code violation to share that circuit.
5. It is not required, but I run a separate 20 amp circuit to the range hood anticipating a future MW at that location.
I suggest you return to the job, run a separate circuit to the range and remove the GFCI if it is behind the refrigerator.
Incidentally, I do not buy this "refrig are better nowadays, so put them on a GFCI." Most of them are much worse...I think you know why.