Please explain to me what surge arresters have to do with pf.
I think he is referencing suppression of cap switch transients
Please explain to me what surge arresters have to do with pf.
I think he is referencing suppression of cap switch transients
Okay, so without looking that up, I am guessing that means something to do with voltage fluctuations causing the capacitors to charge and discharge in a irregular way.
Am I close?
And that voltage transient can have a very low source impedance which puts a lot of stress on surge suppressors.anytime you switch caps you get a surge/transient
Just an unsolicited opinion, but APFC systems are disasters waiting to happen in the modern world where a lot of things have electronics on them, all powered by some form of Switch Mode Power Supply or things like VFDs and Servo amplifiers. The stepping in and out of capacitors will destroy your electronics in short order. One single misstep can wipe out a LOT of expensive equipment in a heartbeat. I was once at a fish processing facility in Alaska where this happened, the APFC unit destroyed over $300,000 worth a VFDs in one second.
It might end up a little more expensive, but FAR safer and more effective, to add what's called "At-Load" power factor correction capacitors. They are sized for each INDIVIDUAL load motor, then wired down stream of the controller so that they are turned on ONLY when that load is turned on, and thereby turned OFF when the load is turned off. I would focus only on the 3 phase machinery for this, single phase induction motors tend to have capacitors already, or are so small as to be insignificant.
But i have some machines like air compressor only start-up (Star-Delta), do you thing needs individual PF correction ?